Is there any way to use analog outputs, that are undefined as closed loop control outputs on an RMC200, without adding a control loop to the feature key? A customer would like to use an output for an open loop command to a proportional relief valve on a pump.

Thanks

---

<div class="post-metadata">

**Author:** ![Jacob\_Paso](https://forum.deltamotion.com/letter_avatar_proxy/v4/letter/j/439d5e/32.png) [@Jacob\_Paso](https://forum.deltamotion.com/u/Jacob_Paso)\
**Post date:** [March 22, 2019, 3:37pm UTC](https://forum.deltamotion.com/t/rmc200-unused-outputs/481/2 "2019-03-22T15:37:53Z")

</div>

Yes, you can create an output-only axis. This is a Control Axis with no loops, and does not use up any feature key loops. An output-only axis does use up one of the axes in the 32-axis limit, but does not use any feature key loops. You can use an output-only axis with open loop commands.

-Jacob