Postby Andyajt » Fri May 23, 2014 9:14 am

I am trying to communicate between Delta and POV.

Is it possible to connect the two?
how do they communicate?
what data formats are used?
Andyajt
 
Posts: 7
Joined: Fri May 23, 2014 9:02 am

Re: Delta and POV (Point of View) communication

Postby Jacob Paso » Fri May 23, 2014 9:34 am

Yes, it is possible to use the Automation Direct Point of View SCADA software with the RMC.

I would recommend using the Modbus/TCP protocol. In RMCTools, wherever an address is listed, you can right-click the address and choose to view it in Modbus format. Use this address when accessing registers in the RMC via Modbus/TCP. You can also find the Modbus addresses for RMC registers in the RMCTools help, in the Register Map topics.

It is also possible to use the Allen-Bradley CSP protocol. The RMC will appear as an SLC/505 PLC to the POV software.
Jacob Paso
 
Posts: 500
Joined: Thu Jan 03, 2008 3:18 pm

Re: Delta and POV (Point of View) communication

Postby Andyajt » Mon Jun 02, 2014 5:43 am

That's great, thank you!
Andyajt
 
Posts: 7
Joined: Fri May 23, 2014 9:02 am

Re: Delta and POV (Point of View) communication

Postby Andyajt » Mon Jun 02, 2014 9:34 am

I am having some difficulties establishing communication with POV.

I have set up my station address in POV (IP address) like so:
192.168.0.100:28683
(28683) being the register: F56:5 converted to Modbus.
I believe it has to be done this way but I am not 100% sure.

I have a program in the RMC already that is being controlled by a CMORE panel.
There are 16 bits/tags in this F56:5 register that the RMC uses so I know where the data needs to go.

I am trying to send data in Hexadecimal to the first 2 bits/tags.
I want the first bit to provide motion in one direction and the second bit to send it back in the other direction.
The CMORE already achieves this but I want to replicate the CMORE with POV, and not use the CMORE.

I hooked up the POV at the same time as the CMORE and tried to command some motion from the POV, but nothing happened.

I am trying to send commands in hexadecimal format via Modbus to register 28683.
Is this the correct method??

I need to understand POV more too, do you have any experience with this??
Andyajt
 
Posts: 7
Joined: Fri May 23, 2014 9:02 am

Re: Delta and POV (Point of View) communication

Postby Jacob Paso » Fri Jun 06, 2014 2:34 pm

When you set up the station address it should be 192.168.0.100:502:1. You do not set the register number here. The register number goes in the IO address column. You will prefix it with 4x:

Beyond that, I can't figure out how to associate the tag with a screen object.
Jacob Paso
 
Posts: 500
Joined: Thu Jan 03, 2008 3:18 pm

Re: Delta and POV (Point of View) communication

Postby Andyajt » Tue Jun 10, 2014 7:28 am

that works!

I can now communicate and read/write to the delta, im happy!!
Andyajt
 
Posts: 7
Joined: Fri May 23, 2014 9:02 am

Re: Delta and POV (Point of View) communication

Postby Andyajt » Tue Jun 10, 2014 7:29 am

thank you!
Andyajt
 
Posts: 7
Joined: Fri May 23, 2014 9:02 am

Re: Delta and POV (Point of View) communication

Postby Jacob Paso » Tue Jun 10, 2014 8:08 am

Could you explain to me the remaining steps to make it communicate, beyond the first step I listed? I would much appreciate it.
Jacob Paso
 
Posts: 500
Joined: Thu Jan 03, 2008 3:18 pm

Re: Delta and POV (Point of View) communication

Postby Andyajt » Fri Jun 20, 2014 9:30 am

The information you gave me was perfect, It worked straight away.
to choose a specific bit you simply place the numbered bit 0-31 after a dot:
for example: 4X:28683.4

to read force you need to change it to Floating Point,
for example: FP:28805

POV has a list of codes to use for each data type.
Andyajt
 
Posts: 7
Joined: Fri May 23, 2014 9:02 am