Greetings,

Ive inherited an ancient mess of an RMC/temposonic system. Ive been trying to sort through the stockpile of old rods.
What would help me greatly is to know which type of rod each RMC is expecting. How do i find which output type each RMC axis is expecting through RMCWIN?

Thanks for your time.

flyingsod,

For the MDT module, in the main RMCWin window, in the Parameter pane, double-click the CONFIG value for the axis. You will see whether it is configured for Start/Stop or PWM.

For the SSI module, in RMCWin, on the Tools menu, choose Module Configuration . In the Slots box, choose the SSI module, then click Slot Options . You will see whether it is Binary of Gray and the number of bits.

For the analog modules, in the main RMCWin window, in the Parameter pane, double-click the CONFIG value for the axis. You will see whether it is configured for voltage or current.

-Jacob

1 Like

That is perfect. Exactly what i need to know. thankyou for the swift reply!