Temposonics II transducers with the Digital Personality Module (DPM) can interface with the RMCs. These transducers need to be configured for External Interrogation which is indicated as the E towards the end of the PN (TTS … DE004)
Steps to use this transducer:
-
Configure as External Interrogation. The manual below contains steps to change the Interrogation method.
550093.pdf (439.3 KB) -
Wire the transducer as External Interrogation. Pins 9 and 10 below must be connected.
-
Configure the RMC’s position feedback as a PWM input.
-
In the RMCTools software scale and offset wizard, include the number of recirculations indicated by the last 3 numbers of the part number. In the example above, the number of recirculations is 4.